IEC60870-104-5 Triggering of Spontaneous message on Point Quality changings

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • IEC60870-104-5 Triggering of Spontaneous message on Point Quality changings
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
sesa45892
Ensign sesa45892 Ensign
Ensign

Posted: ‎2022-03-31 07:21 AM . Last Modified: ‎2023-05-02 11:57 PM

0 Likes
5
1733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-31 07:21 AM . Last Modified: ‎2023-05-02 11:57 PM

IEC60870-104-5 Triggering of Spontaneous message on Point Quality changings

Hi Geo SCADA Expert Community,

Perhaps one of you has a solution to my problem.
I work using EcoStruxure Geo SCADA Expert 2019 June 2021 Update
I try to communicate with EcoStruxure Substation Operation (ESO) using IEC60870-104-5 protocol

I use DNP3 Slave driver from one hand to cummunicate with M580 PLC and IEC60870-104-5 server driver on the other to communicate with ESO.
I transfer a DNP3 Generic Binary Input Point to the IEC60870-104-5 server through a Filtered Bit Value Map. The exchange with ESO is mainly based on the spontaneous messages feature.
This is working fine. Each time the DNP3 BI change of value, a spontaneous message is sent to ESO.
My concern is that if the DNP3 BI becomes Invalid (because of a link failure with the PLC for example) no spontaneous message is sent by the IEC60870-104-5 server to ESO.

My Question: What is the way allow Geo SCADA to trig a spontaneous message reporting the Invalid flag each time the quality of the DNP3 BI changes.

All suggestions is welcomed.
Thanks

  • Tags:
  • dnp3
  • english
  • Filtered Bit Value Map
  • IEC60870-104-5
  • Spontaneous messages
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-04-06 09:19 PM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-06 09:19 PM

I'm unsure exactly how you have your connections configured.

I'm confused by the concept of the DNP3 _slave driver to an M580.

Or "IEC60870-104-5 server driver"

 

If you are using the DNP3 _slave driver (where GSE behaves like a DNP3 _slave device), then if the Quality of the mapped point indicates a non-Good state this should be reflected in the DNP3 point value exposed by the DNP3 _slave driver's 'device'.

If your source point doesn't provide a reliable Quality value that you'd use for this, then you may need to use an Internal Point, and use Logic to manipulate the CurrentQuality of the point to reflect the 'reality'.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa45892
Ensign sesa45892 Ensign
Ensign

Posted: ‎2022-04-12 07:09 AM . Last Modified: ‎2022-04-12 07:21 AM

0 Likes
3
1596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-12 07:09 AM . Last Modified: ‎2022-04-12 07:21 AM

Hi @BevanWeiss 

First, thanks to pay attention to my issue.

Let me be more precise.

 

Dessin1.png

EcoStruxure GeoScada Expert receives information from the M580 PLC using DNP3 protocol.

 

EcoStruxure Substation Operation (ESO) receives information from GeoScada Expert using IEC104 protocol.

 

The GeoSCADA driver is acting like a gateway. The received data from the M580 PLC is sent to ESO by using a Filtered Bit Value Map at the GeoScada Expert level.

 

Each time a bit changes of value in the M580 PLC, a DNP3 Unsolicited message is sent to GeoScada Expert by the M580 PLC and GeoScada Expert retransmits it to ESO through a IEC104 spontaneous message. This is working fine.

 

Now if the communication between GeoScada Expert and the M580 PLC is broken, the quality of the point changes to “no-good” at the GeoScada Expert level but no IEC104 spontaneous message is sent by GeoScada Expert to ESO.

 

Consequence: the data remains with a “good” quality bit at the ESO level. That is not consistent with the reality.

 

My question is how to configure the IEC104 driver of GeoScada Expert to have a sending of the quality bit when the quality bit changes at the GeoScada Expert Level.

 

Thanks.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-04-12 03:52 PM . Last Modified: ‎2022-10-19 12:57 AM

In response to sesa45892
0 Likes
2
1581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-12 03:52 PM . Last Modified: ‎2022-10-19 12:57 AM

Ok, that diagram helps.

 

So you are using the DNP3 driver (GeoSCADA Expert acts as the Master), which means you then get DNP3 points.

These are the items which are showing bad quality due to the comms issue.

 

Then you are using IEC60870 _Slave Driver (GeoSCADA Expert acts as the _Slave/Outstation), which is where the Filtered Value Maps come in.

 

Unfortunately I haven't used the IEC60870 _Slave Driver, and the Value Maps around this fashion.

It might be something that your local Tech Support could answer relatively easily.

 

If the Value Maps don't currently support this then you may need to raise a feature request (or use the Idea Forum here https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/idb-p/geo-scada-expert-ideas) for this idea.

 

The typical way that I'd suggest solving this is to have an integrity poll (period explicit poll) performed from the ESO system.  This should then report the quality state of the point (which should match the referenced DNP3 point quality, i.e. 'bad').

If it doesn't, then you may want to look into the settings you have for the Filtered Value Map to make sure that you don't have it filtering out non-good quality data records.

 

2022-04-13 08_49_10-Window.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa45892
Ensign sesa45892 Ensign
Ensign

Posted: ‎2022-04-14 08:02 AM

In response to BevanWeiss
0 Likes
1
1557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-14 08:02 AM

Hi @BevanWeiss 

 

Again, thanks a lot having considered my requests.

 

Unfortunately, I’ve already explored your proposed solutions before to post.

 

1: An integrity poll on a regular basis seems not possible from the ESO side (I am not aware about ESO, but this was reported to me)

2: The setting of the Filtered Bit Value Map proposes only a generation of event on Value Change, Status Change, Report, End of Period, End of Period Reset, Override or Release but nothing on Quality Change.

 

I hoped for a hidden setting, somewhere …

 

I am going to follow your suggestion and consult the Idea forum.

 

Thanks.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-04-19 06:13 PM

In response to sesa45892
0 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-19 06:13 PM

If ESO can't perform an Integrity poll / period retrieval, then how would it detect if the Geo SCADA Expert server crashed (or was shut down)?

 

What was the result when you tested with the 'Reason for Logging' Event Change Detection and with the Reason Mask set to everything? (you would also need to assign a Class to it for events to be captured).

 

2022-04-20 11_07_35-GeoSCADA Expert 2021 Win2016 - VMware Workstation.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of