Hi,
I wish to have clarification.
We have to connect GeoSCADA to a Web Gateway that will be communicating via SOAPui with XML / Json files.
From what I have read GeoSCADA has no means to de-serialise this format internally?
If this is the case, a Web Server / Client is to built in order to de-serialise the XML files and write values to internal GeoSCADA points via OPC?
(a driver to be created by the DDK).
An additional Web Server / Client cannot be avoided to achieve this path of communications.
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-09 05:18 PM
Correct, you will need to develop an intermediate 'application' which is able to act as a client to both your 'Web Gateway', and also to Geo SCADA Expert / ClearSCADA (whether via SOAP / .NET API / Automation Interface / Simple DDK).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-09 05:18 PM
Correct, you will need to develop an intermediate 'application' which is able to act as a client to both your 'Web Gateway', and also to Geo SCADA Expert / ClearSCADA (whether via SOAP / .NET API / Automation Interface / Simple DDK).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-12 02:12 PM
I believe that my answer has addressed the question that you asked. Please mark it as the solution.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.