Posted: 2025-02-10 05:50 AM
Hello All,
I am getting the following error recently when trying to export a report in GeoSCADA.
"Export report error request failed. Failed to export report, 5.3.3 Unrecognized command."
Note: Configurations have not been changed, and it only affected this report recently. Other reports still work just fine.
What could be the cause and solution to this issue?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 01:31 AM
I presume you're exporting a Crystal Report. I would expect the event message to be formatted slightly differently:
"Export report request failed - Failed to export report, <error> (<time>)"
I also presume you're exporting to an email destination. The "5.3.3 Unrecognized command" error is coming from your mail server (probably Microsoft Exchange). A search shows lots of information about this error:
https://www.google.co.uk/search?q=5.3.3+Unrecognized+command
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 01:31 AM
I presume you're exporting a Crystal Report. I would expect the event message to be formatted slightly differently:
"Export report request failed - Failed to export report, <error> (<time>)"
I also presume you're exporting to an email destination. The "5.3.3 Unrecognized command" error is coming from your mail server (probably Microsoft Exchange). A search shows lots of information about this error:
https://www.google.co.uk/search?q=5.3.3+Unrecognized+command
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-13 05:17 AM
Thank you @AndrewScott for the response. That is correct, I was trying to export to an email destination. The odd thing is that it only affected this one report. I have other reports that worked just fine. There was no configuration changes since the error occurred.