Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Exclude Points from Embedded Alarm List/Areas of Interest on Calculated points

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Exclude Points from Embedded Alarm List/Areas of Interest on Calculated points
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
MichaelAur
Ensign MichaelAur
Ensign

Posted: ‎2025-03-07 02:03 AM

0 Likes
3
754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 02:03 AM

Exclude Points from Embedded Alarm List/Areas of Interest on Calculated points

Hi All,

We currently display all alarms in a big embedded alarms list. This is beginning to become a little unwieldy. We were hoping to filter out some of the less urgent alarms into a secondary alarms list. I had thought that 'Areas of Interest' would be a perfect solution here.  I had hoped to make areas of interest like below and then set our 'Normal' alarms list show only 'Important' points of interest and then another alarms list that shows the less important Items.

  World

  • Important (Set to default)
  • Less Important

However, we also use Calculated points to trigger a number of our alarms, and it doesn't seem you can assign areas of interest to these? So when I modify our normal list to only show Important areas of interest it skips all these calculated point as they are in the top level 'World' group.

As such I was wondering if anyone could think of a good way to be able to have these two separate alarm lists?

Thanks.
Ps we are currently using Geo Scada Expert 2021, March 2024 Update (84.8852)

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
tfranklin
Commander tfranklin
Commander

Posted: ‎2025-03-07 11:42 AM

1 Like
1
731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 11:42 AM

So the first part of your question -- calculated points do indeed have areas of interest.  You configure them on the analog point / digital point tabs under the limits category. 

 

One thing to note with AOI is that any alarmable type will have its own independent AOI, so this may add to some configuration for you to manage. You can use AOI for this, but the issue is that if you determine an AOI on a point is "not important" and classify it as such, the whole item is now not important.  That might not be the desired behavior -- maybe only the low alarm is not important, but if it goes to high high -- I need people to know.

 

What you described though of normal vs important alarms is exactly what severities are for.  By default GS comes with low, medium, high, and critical.  There's nothing to stop you from creation additional classifications though then using filters on your alarm lists for filtering out low severity items.

 

A popular configuration here in the US (and likely elsewhere) is that users will often have severities < 100 be for notifications or things the SCADA team is responsible for, but anything >= 100 will be for operators/controllers.  This allows us to configure severities on a limit by limit basis and only show what's required to the users.  This allows you to set severity levels on different state values and the filters are respected as such in the alarm lists. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
tfranklin
Commander tfranklin
Commander

Posted: ‎2025-03-07 11:42 AM

1 Like
1
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 11:42 AM

So the first part of your question -- calculated points do indeed have areas of interest.  You configure them on the analog point / digital point tabs under the limits category. 

 

One thing to note with AOI is that any alarmable type will have its own independent AOI, so this may add to some configuration for you to manage. You can use AOI for this, but the issue is that if you determine an AOI on a point is "not important" and classify it as such, the whole item is now not important.  That might not be the desired behavior -- maybe only the low alarm is not important, but if it goes to high high -- I need people to know.

 

What you described though of normal vs important alarms is exactly what severities are for.  By default GS comes with low, medium, high, and critical.  There's nothing to stop you from creation additional classifications though then using filters on your alarm lists for filtering out low severity items.

 

A popular configuration here in the US (and likely elsewhere) is that users will often have severities < 100 be for notifications or things the SCADA team is responsible for, but anything >= 100 will be for operators/controllers.  This allows us to configure severities on a limit by limit basis and only show what's required to the users.  This allows you to set severity levels on different state values and the filters are respected as such in the alarm lists. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MichaelAur
Ensign MichaelAur
Ensign

Posted: ‎2025-03-07 08:56 PM

In response to tfranklin
0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 08:56 PM

Hey Tfranklin. Thats a little embarrassing on my side. When I was looking through Bulk edit options I didnt see the areas of interest. But I now see that it is under 'StateAreaOfInterestID'! vs most of the other data points being 'AreaOfInterestID'

 

As for the adjusting the levels of alarms. This is probably a case of putting the horse before the cart. But our users want to preserve the severities level but just have them in a separate tab. Thankfully in this case the users do indeed want any alarms from this one object/point to be shunted into its own screen. So I just thought areas of interest (which we havenet been using) might be the easiest option. But by keeping the top level 'World' group if we ever want I can just change the main alarms list to display 'world' area of interest. 

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-03-10 06:25 PM

1 Like
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 06:25 PM

You'll find the extra AreaOfInterestID fields when the object has multiple alarm subconditions and it makes sense for them to have different AOIs

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore