Dynamic SQL query

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Dynamic SQL query
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
kapla
Crewman kapla
Crewman

Posted: ‎2024-08-19 02:02 AM

0 Likes
5
1489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-19 02:02 AM

Dynamic SQL query

Hi,

Is it possible to access specific variables in SQL with a dynamic link in ST ?

I can access specific variable in a folder or a group with the SQL querries but I need to tell where to search or it would be too generic.

For example if I have multiple site with the same tree : SiteX/DeviceX/power_setpoint

(power setpoint is a generic DNP3 output)

And I would like to get in a ST program the value of power setpoint if it exist in SiteX.

 ie: QueryState3 AT %S(SELECT Id,FullName,OutstationId FROM CDNP3AnalogOut WHERE FullName LIKE '%.%.%.testbench.%') : RESULTSET OF Point3;
At this moment I use a query but I need to change the query in each Site to match SiteX :

I know we can use {link} in VAR declaration and link in input but I can't make a fusion of both.

ie: P_FCR1 AT%I({Link1}.CAP1.R_CS_FCR_Cap.Pa_RT):DINT;

Is it possible to have one same ST who can use a query to check one specific Site.

 

For example in ST program 1 I got this:

 QueryState3 AT %S(SELECT Id,FullName,OutstationId FROM CDNP3AnalogOut WHERE FullName LIKE '%.%.%.testbench.%') : RESULTSET OF Point3;

I would like to have a dynamic variable (name link for example) to replace %.%.%.testbench.% by and so I can set this variable link to %.%.%.testbench.% outside the ST program (in ST program 2)

Labels
  • Labels:
  • DNP3
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-08-20 02:44 AM . Last Modified: ‎2024-08-20 02:46 AM

1 Like
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-20 02:44 AM . Last Modified: ‎2024-08-20 02:46 AM

See https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Accessing-Data-via-SQL-in-Structured-Text/ba-p/... for how you can do what I think you're trying to do.

 

You'll have to have a calling logic program to pass in the relevant variables for each site as the dynamicness need to come from the VAR_INPUT block not the VAR block

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-08-20 02:44 AM . Last Modified: ‎2024-08-20 02:46 AM

1 Like
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-20 02:44 AM . Last Modified: ‎2024-08-20 02:46 AM

See https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Accessing-Data-via-SQL-in-Structured-Text/ba-p/... for how you can do what I think you're trying to do.

 

You'll have to have a calling logic program to pass in the relevant variables for each site as the dynamicness need to come from the VAR_INPUT block not the VAR block

Reply

Link copied. Please paste this link to share this article on your social media post.

kapla
Crewman kapla
Crewman

Posted: ‎2024-08-26 12:42 AM

0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-26 12:42 AM

Thanks Adam, 

It's working well.

I was trying to use the VAR_INPUT but I didn't check correctly the WITH_PARAMS.

So now I got my site (string) in input, I need to concat the site Name and '.%' before then I use this string as param in my query and everything work like a charm.

ex:

QueryState AT %M(SELECT Id,FullName,CurrentValue,OutstationId FROM CDNP3AnalogIn WHERE FullName LIKE ?) : RESULTSET OF Point WITH_PARAMS Link;

 

With Link as my site FullName.%

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-08-29 03:01 PM

1 Like
1
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-29 03:01 PM

The double bar || is the SQL concatenate function, in the resource centre article there is an example of this

 

Points AT %S(SELECT Id, FullName, CurrentValue FROM CPointAlgManual WHERE FullName LIKE '%' || ? OR FullName LIKE ? || '%') : RESULTSET OF Point WITH_PARAMS Name, Name;
Reply

Link copied. Please paste this link to share this article on your social media post.

kapla
Crewman kapla
Crewman

Posted: ‎2024-08-30 05:42 AM

In response to AdamWoodlandToo
0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 05:42 AM

Thanks,

Do you know if it's possible to use WITH_PARAMS to adress a specific Data Table not just to specify the values.

Like not declare it but with a '?' and a Var_input ?

"D1 AT %D(DELETE FROM table01);" from this 

"D1 AT %D(DELETE FROM ?) WITH_PARAMS linkTable01;" to this 


 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-09-02 01:47 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-02 01:47 AM

No, it is not possible to do that - the tables in the query are fixed. Perhaps use a system command to run an external program for this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore