Display Point Data on a Trend Only When Another Point is a Specified Value

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Display Point Data on a Trend Only When Another Point is a Specified Value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
SurprisedEwe1
Ensign SurprisedEwe1
Ensign

Posted: ‎2024-12-08 11:21 PM

0 Likes
3
1293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-08 11:21 PM

Display Point Data on a Trend Only When Another Point is a Specified Value

Is it possible to display a trend line for a historically recorded data point when another point is a particular value (such as a digital)?

 

In incredibly simple SQL terms this would be showing the returned data for:

SELECT AnalogueTagValue
FROM HISTORIAN
WHERE DigitalTagValue = 1

 

The scenario for this is that for a flowmeter that has an analogue flow value it has a digital value indicating the direction. Operations want to only see on a trend the flow when it is in or out only - i.e. the digital direction value is high, so the analogue value displayed corresponds to inflow and they would like that displayed on a particular trend. If the direction is low (outflow) then we show the trend value as 0. Vice versa, a trend could display the outflow when the digital is low.

 

I understand this could be done a multitude of ways by collecting the data in another point (such as using logic in the RTU or scripting to an internal point etc.), however for brevity and reducing the data stored in the historian the equivalent of a view would be nice if possible since the data is already captured, this is purely a visualisation task on the raw data. The task of making the modification would also be simpler if a SCADA solution is possible.

 

I was hoping that using some form of Historic Algorithm or View in the server may have allowed this and I have considered using the "Put Aside" method on the historical data by performing an override on the data when the digital is a particular value (such as overriding to 0 then having the put aside values as one of the directions), however this seems more effort than it's worth and only provides a single direction when we would like both.

Labels
  • Labels:
  • Trends
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-12-12 04:15 AM

0 Likes
2
1251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 04:15 AM

I can't think of another way to do this - the simplest seems to be to create a separate analog point.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

SurprisedEwe1
Ensign SurprisedEwe1
Ensign

Posted: ‎2024-12-16 06:57 PM

In response to sbeadle
0 Likes
1
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-16 06:57 PM

Thanks Steve. I think that the best solution in our context is using Calculated Points.

 

One calculated point will be used for "In Flow" where it is the analogue value multiplied by the digital value, the other is for "Out Flow" which is then the analogue value multiplied by the inverse of the digital value. Then each calculated point can be used by operations as a trend line. These points will then be set as Historical but only captured by Geo SCADA and not the Client's other historian platform (this continues to only capture and store the analogue flow and the digital direction).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-12-12 04:15 AM

0 Likes
2
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 04:15 AM

I can't think of another way to do this - the simplest seems to be to create a separate analog point.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

SurprisedEwe1
Ensign SurprisedEwe1
Ensign

Posted: ‎2024-12-16 06:57 PM

In response to sbeadle
0 Likes
1
1190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-16 06:57 PM

Thanks Steve. I think that the best solution in our context is using Calculated Points.

 

One calculated point will be used for "In Flow" where it is the analogue value multiplied by the digital value, the other is for "Out Flow" which is then the analogue value multiplied by the inverse of the digital value. Then each calculated point can be used by operations as a trend line. These points will then be set as Historical but only captured by Geo SCADA and not the Client's other historian platform (this continues to only capture and store the analogue flow and the digital direction).

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkPitout
Lieutenant JG MarkPitout Lieutenant JG
Lieutenant JG

Posted: ‎2024-12-18 04:35 AM

In response to SurprisedEwe1
2 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-18 04:35 AM

Hi @SurprisedEwe1,

I see you arrived at the same conclusion I had in my head. But, for the fun of it, I made a simulation for your situation (attached).

For interest, the calculations I configured in the calculated points are:

 

Inflow:

IIF( ".Direction.CurrentValue", ".Flow.CurrentValue", 0 )

 

Outflow:

IIF(NOT ".Direction.CurrentValue", ".Flow.CurrentValue", 0 )

 

Be sure to set the significant change config of the calculated points to "None", or you might end up with small residual values retained in the points (eg. Outflow value is 50.0, but Inflow value is also 0.045, when it should be 0.0). 

MarkPitout_0-1734525113007.png

 

Below a screenshot from my simulation:

MarkPitout_1-1734525153734.png

 

 

Attachments
Flow Meter Direction 2024-12-18.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore