Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Defining a user method to bring up default file open dialog box

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Defining a user method to bring up default file open dialog box
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
103
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
rlao
rlao
Contributor

Posted: ‎2024-10-14 11:44 PM . Last Modified: ‎2024-10-15 12:21 AM

0 Likes
4
1416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-14 11:44 PM . Last Modified: ‎2024-10-15 12:21 AM

Defining a user method to bring up default file open dialog box

Hi all,

 

I have a use case for GS2023 Aug 2024 where I am trying to make the methods of the x70 outstation configuration object accessible via the object menu of the corresponding x70 outstation object. This is so that engineering users do not have to hunt for the configuration object to do actions like importing in logic or generating rtz configs for an outstation.

 

Defining a custom user method gets me most of the way there, but I can't seem to leave the method arguments blank so that the default dialog box comes up asking for missing user input. Defining the method call as a user method pick action within a mimic gets me exactly what I want which is the below dialog box:

rlao_0-1728973957813.png

 

However, I am unable to replicate this exact behaviour as a user method on the actual x70 outstation object itself. The closest I can get is to define a prompt (e.g. ImportRTZ(['Filename',''],4)) but it just asks for generic string input and I do not get access to browse the file system for an rtz file. Hence, the built-in dialog box above is much more preferable for me.

 

Just wondering if there is a way to achieve what I need, thanks!

Labels
  • Labels:
  • SCADA
  • Telemetry
  • Tags:
  • User Methods
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2024-11-07 02:26 AM

0 Likes
0
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 02:26 AM

No further activity on this item. Marking as Solved to close it. Please create another posting to discuss further.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
AndrewScott
AndrewScott
Leader

Posted: ‎2024-10-17 08:01 AM

0 Likes
1
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 08:01 AM

User method prompts don't have any support for file arguments, so you can't do this with a user method.

 

Locating the SCADAPack x70 Device associated with a SCADAPack x70 DNP3 Outstation shouldn't require any hunting. Just open the outstation's properties, click on the "Go To" button and then click "Locate in Database Explorer" menu option (in document tab's menu). This will navigate the Database Explorer to the device.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
rlao
Contributor

Posted: ‎2024-10-21 01:14 AM

In response to AndrewScott
0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 01:14 AM

Hi @AndrewScott,

 

Thanks for your quick response and very much appreciated.

 

To respond to your latter point and explain my point of view: our field techs are used to the E-Series interface where the config and outstation were a single object with a consolidated menu, rather than split. So their expectation was they can drive everything from the one convenient menu, from refreshing outstation to generating config files.

 

The x70 interface may be a struggle for them to adapt. I want to keep in mind that they are out in the field and they may not always be generating config files every day. So I want to streamline this as much as possible for their benefit, to minimize the number of 'clicks' that they have to remember while they are probably not in the most comfortable of environments.

 

The workflow is simple for us engineers but for field techs, they would have to remember to:

  • Open Properties from the x70 Outstation object menu.
  • Click 'Go To' on the x70 Device field to bring up the linked config object properties.
  • Right click on the tab of the config properties and click Locate in Database Explorer.
  • Right click the config object in the database bar and hit Export to RemoteConnect, then navigate to a file location to save the exported rtz file.

The E-Series method may not be a one-click process itself either. However, the workflow importantly was localized to within a single popup box hence no need to open additional forms and select additional database objects:

  • Open Configuration Setup from the E-Series Outstation object menu
  • Click Generate on the Configuration Setup popup window, then click OK immediately after.
  • Click Export and navigate to a file location to save the exported rtu file.

Hence, why I was trying to see if I could invoke the config object ExportRTZ method directly as a pick action on the outstation object. This would reduce the x70 workflow from four steps to practically just one.

 

However, more importantly you indicated that what I am trying to achieve is not possible so I think my next best bet is simply a custom menu that brings up both outstation and config object menus.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2024-10-24 04:57 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 04:57 AM

Can VBscript create a windows scripting host to list the files in a folder? Then script could populate a drop-down with the filenames.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2024-11-07 02:26 AM

0 Likes
0
1215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 02:26 AM

No further activity on this item. Marking as Solved to close it. Please create another posting to discuss further.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore