Data export through ODBC to other database

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Data export through ODBC to other database
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
FrankCZ
Crewman FrankCZ
Crewman

Posted: ‎2023-01-16 06:17 AM . Last Modified: ‎2023-05-02 11:49 PM

0 Likes
2
1940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-16 06:17 AM . Last Modified: ‎2023-05-02 11:49 PM

Data export through ODBC to other database

Hi all,

We use SCX – Geo Scada Expert 2021 – build 84. We use SQL export to TXT file. We have set up ODBC connection as well and if we use SQL command, we can export some variables to MS Excel. There are only time, date, name of station and value of minimum flow per day.

Our vision is, that would like to use / present time series with „Graphana „ – but Graphana is tool for view some values – these values are saved in database, but Graphana has not ODBC connector.

So, we would like to ask YOU, if somebody has ever solved some „data pump“ from SCX database to other database help with ODBC ? Could you, please, share some idea ?

Our idea is like some „data pump“ connect through ODBC driver/connection to SCX database and with SQL command (we have already) save data from SQL command to some other database, which Graphana is able to use as a source of data. Graphana is open source dashboard for analytics and visualization.

 

We have set up ODBC connection - Clear SCADA driver.

 

Thank you for any comments


Frank

Labels
  • Labels:
  • SCADA
  • Trends
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: ‎2023-01-17 10:26 AM

0 Likes
1
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-17 10:26 AM

Here is one way this can be done, using SQL Server

1. Install the ClearSCADA/GeoSCADA data components on the SQL server you are planning to extract data

2. The above would install the "Configure Connections" utility. Open that and set up a connection to the GeoSCADA server and also set up a system name

3. Set up ODBC source (64 bit preferable) and use the System Name created in Step 2

4. Set up a linked server in SQL, using the ODBC source. In the security provide user credentials that can run queries on GeoSCADA. This user MUST exist in GeoSCADA and have the necessary access permissions. If you are able to create the linked server, without any errors, then you can try to "test" it using the "test connection" option from SQL Sever

5. Once the connection is good, you should be able to use openquery to retrieve from data from GeoSCADA:

Select * from openquery(<name of linked server>, 'Select FullName, Name from CDBPoint where Id = 1234567')

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: ‎2023-01-17 10:26 AM

0 Likes
1
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-17 10:26 AM

Here is one way this can be done, using SQL Server

1. Install the ClearSCADA/GeoSCADA data components on the SQL server you are planning to extract data

2. The above would install the "Configure Connections" utility. Open that and set up a connection to the GeoSCADA server and also set up a system name

3. Set up ODBC source (64 bit preferable) and use the System Name created in Step 2

4. Set up a linked server in SQL, using the ODBC source. In the security provide user credentials that can run queries on GeoSCADA. This user MUST exist in GeoSCADA and have the necessary access permissions. If you are able to create the linked server, without any errors, then you can try to "test" it using the "test connection" option from SQL Sever

5. Once the connection is good, you should be able to use openquery to retrieve from data from GeoSCADA:

Select * from openquery(<name of linked server>, 'Select FullName, Name from CDBPoint where Id = 1234567')

Reply

Link copied. Please paste this link to share this article on your social media post.

FrankCZ
Crewman FrankCZ
Crewman

Posted: ‎2023-01-22 11:58 PM

In response to tkswathik
0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-22 11:58 PM

Thank you for advice, we try it !

 

BR

 

F

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore