DNP3 lost communication Gescada/NOR

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • DNP3 lost communication Gescada/NOR
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
kapla
Crewman kapla
Crewman

Posted: ‎2024-10-18 01:09 PM

0 Likes
1
914
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-18 01:09 PM

DNP3 lost communication Gescada/NOR

Hi,

Since a few months we got a lot of connection error between site and scada (we change from Clearscad to Geoscada).

We now have Geoscada and communicate with DNP3 trough a VPN connection provide by a router to a M340 with a BMX NOR 0200.

All our site are similar.

But on all site we got each day many loss of data between few seconds to hours.

The connection is assure by a router with a VPN and this one doesn't indicate any loss of internet acces.

Even during test, we are connect to the plc with the router and VPN but we lost DNP3 connection (port 2000) but not the plc connection (port 502).

I try to check and understand as many of parameters as I can but now I don't know where the problem is, like my Reestablishment Interval is about 300s but it doesn't seem to work.

For example as each time we got a connection error, I just have to delete the @IP or the Outstation adress save, reput what I've delete and save and the connection fall healthy.

Have you got any idea on that ? 

Labels
  • Labels:
  • DNP3
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-10-21 09:28 AM

1 Like
0
892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 09:28 AM

To investigate an issue like this will need access to the Geo SCADA DNP3 driver logs, event journal messages and possibly a copy of your configuration (channel, set and outstation). The "I/O" logging option will need to be enabled on the DNP3 driver, see Define the Driver Logging Settings. A comms log for the channel would also be helpful, see Enable or Disable 'Normal' Communications Logging on a Channel.

 

If you pass this information to SE support they will be able to analyse the log files and provide advice.

 

Its not clear from the issue description whether this is a network problem (e.g. TCP connection is failing), or a problem communicating with the DNP3 outstation (e.g. timeout, no reply, incorrect reply).

 

Making a 'significant' configuration change to the outstation will cause the driver to delete and recreate the outstation within the driver. This will create a new TCP connection (assuming your using TCP and not UDP) and perform the DNP3 start-up sequence which varies depending on how the outstation is configured.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-10-21 09:28 AM

1 Like
0
893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 09:28 AM

To investigate an issue like this will need access to the Geo SCADA DNP3 driver logs, event journal messages and possibly a copy of your configuration (channel, set and outstation). The "I/O" logging option will need to be enabled on the DNP3 driver, see Define the Driver Logging Settings. A comms log for the channel would also be helpful, see Enable or Disable 'Normal' Communications Logging on a Channel.

 

If you pass this information to SE support they will be able to analyse the log files and provide advice.

 

Its not clear from the issue description whether this is a network problem (e.g. TCP connection is failing), or a problem communicating with the DNP3 outstation (e.g. timeout, no reply, incorrect reply).

 

Making a 'significant' configuration change to the outstation will cause the driver to delete and recreate the outstation within the driver. This will create a new TCP connection (assuming your using TCP and not UDP) and perform the DNP3 start-up sequence which varies depending on how the outstation is configured.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore