Automatic creation of items in global mimic

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Automatic creation of items in global mimic
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Tyrone19
Lieutenant Tyrone19 Lieutenant
Lieutenant

Posted: ‎2021-09-17 02:43 AM . Last Modified: ‎2023-05-03 12:01 AM

0 Likes
3
1782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-17 02:43 AM . Last Modified: ‎2023-05-03 12:01 AM

Automatic creation of items in global mimic

Hi Community

 

Does anyone know how to get Geoscada to automatically add entries onto a Global mimic. 

 

For example if I have a Group called Demo. Demo would have 1 global mimic and every time I add an instance of a template a block would get added to the global mimic automatically and this tied automatically to the instance details.

 

Thanks 

Labels
  • Labels:
  • Drivers
  • SCADA
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-09-17 09:45 PM

0 Likes
2
1774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-17 09:45 PM

There's no straight forward way to do this in a 'complex' graphical sense.

 

What tends to be the way to achieve this is:

a. Use an embedded query to display the list of sites, such that when the new site instance is created the embedded query will reflect the existence of this site.

b. Use map displays, so that the query that drives the map is updated with the new site, and hence the site now appears on the map.  NOTE: Maps can't be embedded, so you end up having a whole popup window for such a mapping interface.

 

It is possible to have automation that modifies a mimic to add such a site, but it's not recommended.

There's only one customer that I've been involved in doing this for, and the return on investment just wasn't there... the squeeze was not worth the juice.

You'd want to look into the ViewX automation for this.  It's not supported, not well documented, and has had some bugs in the past (which given the not supported aspect aren't guaranteed to get a speedy resolution).  It's also really hard to maintain.

 

Plus it requires a ViewX installation, and a ViewX licence to do it.  If you're manually creating sites, sure you might already have that.  But if you're creating sites using the .NET API (i.e. because you're creating them in the dozens.. or automatically) then ViewX isn't a guarantee.

 

 

There's lots of ways to do tricky things which get close enough to what you want without all the effort.

For instance, if the user just wants to know where a site is.. you can have the query list, and when they select a site, you dynamically update a remote image URL so that it pulls down a static google map image with a marker at the GPS co-ords of the site in question.  Relatively easy to do... and looks cool.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Tyrone19
Lieutenant Tyrone19 Lieutenant
Lieutenant

Posted: ‎2021-09-18 09:26 AM . Last Modified: ‎2021-09-18 09:30 AM

In response to BevanWeiss
0 Likes
1
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-18 09:26 AM . Last Modified: ‎2021-09-18 09:30 AM

Hi Bevan

 

Thanks for the reply.

 

With regards to the last option- how would I go about doing the dynamic updating and pulling out a static image with the correct GPS location. Would this require some VB coding?

 

Thanks

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-09-18 09:35 PM

In response to Tyrone19
1 Like
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-18 09:35 PM

Yeah it would need some VBscript / JScript.

 

You'd essentially have a small script associated with the embedded query, so when it's clicked it goes and gets the GeoLocation of the site clicked. If you have the lat/long as hidden columns in the embedded query this is even easier.

Embedded queries already have stuff for this.. so it's relatively easy (if you do the hidden columns and are using a newish version of GeoSCADA I'd possibly label it 'trivial')

 

Then you update the RemoteUrl (or whatever the correct animation param on the remote image is).. or you update a registry value with the lat/long with that reg value used in the remote image animation.

 

Updating the registry is definitely the easy way here too.. you could do it with like half a dozen lines of code (I want to say 3 lines, but error handling would add a couple too).

 

The static image is just how remote image works. You give it a url, it displays the image at the url.

Google maps static images does the heavy lifting of the rest (you just need to feed it an appropriate URL.. which will require a Google API key).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore