Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Assistance with Connecting TIA Portal to GeoSCADA via OPC

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Assistance with Connecting TIA Portal to GeoSCADA via OPC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
336
AndrewScott
AndrewScott
127
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Mehdi_Sajjadi
Mehdi_Sajjadi
Contributor

Posted: ‎2025-10-15 04:56 AM

0 Likes
4
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 04:56 AM

Assistance with Connecting TIA Portal to GeoSCADA via OPC

Hi,

I’ve been away from GeoSCADA for a while and recently started refreshing and upgrading my knowledge. I’m currently working on connecting the TIA Portal to GeoSCADA and have found that OPC UA appears to be the primary method for integration.

 

Within GeoSCADA, I’ve noticed there are four different types of OPC connections, and I’m unsure whether I should be using OPC UA or OPC Simple. Additionally, I’m unclear on how to properly define a "Server" and a "Scanner" in this context.

 

Could you provide some guidance on how to configure these components within GeoSCADA? Also, are there any considerations I should be aware of on the Kepware side?

 

Thanks in advance for your help.

 

Best regards,

Labels
  • Labels:
  • Drivers
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
BevanWeiss
Champion

Posted: ‎2025-10-15 10:02 PM

1 Like
2
2040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 10:02 PM

Having the TIA Portal PLC (you haven't mentioned which PLC you're actually using) as an OPC-UA Server, and then having GeoSCADA Expert as the OPC-UA Client reading the tags from the PLC (Server) is the way that I would suggest here.

 

You would want to reference the help for creating OPC-UA Client connections.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BevanWeiss
BevanWeiss
Champion

Posted: ‎2025-10-15 10:02 PM

1 Like
2
2041
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 10:02 PM

Having the TIA Portal PLC (you haven't mentioned which PLC you're actually using) as an OPC-UA Server, and then having GeoSCADA Expert as the OPC-UA Client reading the tags from the PLC (Server) is the way that I would suggest here.

 

You would want to reference the help for creating OPC-UA Client connections.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2025-10-17 02:01 AM

1 Like
0
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-17 02:01 AM

Press F1 for help, max the window, look at the left hand tree for Driver Reference / OPC UA Driver.

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Mehdi_Sajjadi
Contributor

Posted: ‎2025-10-18 06:03 AM

In response to BevanWeiss
0 Likes
0
1952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-18 06:03 AM

Thanks BevanWeiss

 

I’ve mainly used Geo SCADA with DNP3, and I’m new to OPC. I’m trying to set up communication between Geo SCADA and a simulated S7-1511-1 PN PLC (via TIA Portal v19 and PLCSIM Advanced V6 connected to Kepware V6) but haven’t succeeded yet. I’m using the Geo SCADA trial (1000-tag) version and looking for a simple way to establish this connection for learning purposes

 

Thanks in advnace

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Mehdi_Sajjadi
Contributor

Posted: ‎2025-10-21 02:29 AM

In response to BevanWeiss
0 Likes
0
1952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-21 02:29 AM

It's all set now. I was initially confused between the different OPC UA options, but I've figured out that OPC Simple is the right one to use—and it's working perfectly

 

Appreciate it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore