App.AutoLogOff

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • App.AutoLogOff
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
ErikBouthillier
ErikBouthillier
Cadet

Posted: ‎2019-12-18 09:49 AM . Last Modified: ‎2023-05-03 12:19 AM

0 Likes
4
3362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 09:49 AM . Last Modified: ‎2023-05-03 12:19 AM

App.AutoLogOff

I need to log everyone off all the ViewX clients at the end of every shift change. How can I do this. I tried to use the scheduler to trigger a System command but still would not work. Any suggestions would be great.

Labels
  • Labels:
  • SCADA
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2019-12-18 07:09 PM

1 Like
2
3348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 07:09 PM

You can do this by setting .AccountEnabled to False (then set it back to True if you want them to be able to log in later). You might want to check .IsLoggedIn is going False before re-enabling, to make sure the change has gone through.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2019-12-18 07:17 PM

In response to Anonymous user
1 Like
1
3345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 07:17 PM

@Anonymous user 

To build on what Jesse has said, my recommendation would be to have a set of User Groups for each 'shift'.

Then you can have a schedule which will trigger some ST logic.  The ST logic would enumerate through all of the users within that Shift, and Disable the Accounts.  Other logic could enable the accounts for the next appropriate Shift.

This way only the people 'on shift' would be able to log into Geo SCADA Expert.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-18 10:25 AM

0 Likes
0
3359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 10:25 AM

You could use the User Object > Security Tab > Inactivity Logout to automatically log the user off if they (or the next shift) are not moving the mouse around. Has the added side effect of logging them out mid shift if they are not active during the shift if Inactivity Logout time is too short. And also the down side of not working if the work station is occupied by the next shift (24 hour 365 day a year operations in my case). 

 

I ran into some interesting details when I wanted to do something similar. I wanted to keep the controllers from forgetting to logout and the next controller from using the previous controller's account on the same workstation, so the Inactivity method wouldn't work for me. So I needed some kind of notification if someone was logged in for more than 12.5 hours (slightly more than a typical shift). And I wanted a way to ensure that at the beginning of the shift, the sound on the work station was tested. 

 

I ended up making a simple Function Block Diagram and 2 internal points for each user to accomplish this. Unfortunately I have never found a way of successfully logging off a user who did not logoff themselves and their work station is still in use. But having the FBD update a point and cause an alarm if a user has been logged in for too long, at a minimum should get the controller on the next shift to realize they may be using the wrong account and to login to their account. And playing a test sound after a new user login ensures that the previous controller did not turn the sound off or down to super low.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-18 07:09 PM

1 Like
2
3349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 07:09 PM

You can do this by setting .AccountEnabled to False (then set it back to True if you want them to be able to log in later). You might want to check .IsLoggedIn is going False before re-enabling, to make sure the change has gone through.

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2019-12-18 07:17 PM

In response to Anonymous user
1 Like
1
3346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-18 07:17 PM

@Anonymous user 

To build on what Jesse has said, my recommendation would be to have a set of User Groups for each 'shift'.

Then you can have a schedule which will trigger some ST logic.  The ST logic would enumerate through all of the users within that Shift, and Disable the Accounts.  Other logic could enable the accounts for the next appropriate Shift.

This way only the people 'on shift' would be able to log into Geo SCADA Expert.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-19 06:12 AM

In response to BevanWeiss
0 Likes
0
3332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-19 06:12 AM

@BevanWeiss That is an interesting idea and could be quite useful. For me, I think I will avoid the disabling the account until they are on shift just due to the nature of the controllers rotating 28 day schedules with so many daylight shifts and so many night shifts during the 28 days, and coverage for vacations and sick days etc where a controller works a non scheduled day. But still quite a useful idea.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore