Posted: 2024-08-07 05:12 PM
We have Schneider Automation Server with Andover Continumm B3810 series. In the webstation the web graphics is displaying an error message pop up "Script error in DocumentLoadEvent(Bind) ReferenceError:MutationEvent is not defined do you want to continue script." After we click "Ok" it still keeps popping up. Also the graphics is not loading value. For example, OAT reading XXX.
Could you please assist in resolving this display error in the PC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 04:19 PM
Hi Team,
We had the same issue at a site here. The issue is something to do with Mutation Events inside of chrome and Microsoft Edge. We have found a solution in the browsers with "flags"
When the page reloads it should work again.
Link below is where I found the fix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 11:33 AM
We are getting the same issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 04:19 PM
Hi Team,
We had the same issue at a site here. The issue is something to do with Mutation Events inside of chrome and Microsoft Edge. We have found a solution in the browsers with "flags"
When the page reloads it should work again.
Link below is where I found the fix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-12 05:32 PM
@treesa21 this is a known issue in EBO. "MutationEvent is not defined" Javascript errors are displayed after Chromium based browsers (Chrome or Microsoft Edge) are updated to version 127.
As referenced in Mutation events will be removed from Chrome | Blog | Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function. EBO hotfixes are available for all currently supported EBO versions, your local EBO System Integrator or SE branch will have access to the hotfixes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-24 11:43 PM
Thank you very much for this really helpful solution. I met the same issue with the Web access to EBO.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-14 12:24 AM
Thanks for your valuable information
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-22 08:15 PM
Hi @CraigEl,
We have Enterprise Server 3.3.1.2301 installed on our building.
We have problems with our local EBO System Integrator and does not want to apply hotfix.
Can you provide us the link to the hotfix so I can apply it?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-06 05:17 AM
The same issue on this site where we are running version 6.
Resolved it with the helpful solution of above on Chrome and Edge, will run the Hotfix on the Server as well.
Kind regards,