POU, Data Type & Function utilization in EAE application

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • POU, Data Type & Function utilization in EAE application
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Automation Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Start a Topic
Solved
anandbpillai
Ensign anandbpillai Ensign
Ensign

Posted: ‎2021-10-11 09:22 PM . Last Modified: ‎2023-07-28 02:24 AM

0 Likes
4
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-11 09:22 PM . Last Modified: ‎2023-07-28 02:24 AM

POU, Data Type & Function utilization in EAE application

There is POU, Data Type & Function available in the EAE application but not sure what is the exact purpose and how it is to be mapped in any application.

The help also is not that useful for this topics.

Pls provide any support or document reference for this.

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PatrickJouvenel
Crewman PatrickJouvenel Crewman
Crewman

Posted: ‎2021-11-10 06:54 AM

In response to anandbpillai
2 Likes
0
2350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-10 06:54 AM

for Datatype is quite straightforward:

- enumeration 

TYPE DataType3 : (item1,item2,item3);END_TYPE

- alias

TYPE DataType2 : BOOL; END_TYPE

-struct

TYPE DataType1 : STRUCT 
item1  : BOOL;
item2  : REAL;
item3  : STRING;
 END_STRUCT;
END_TYPE

-array

TYPE DataType5 : ARRAY[0..4] OF BOOL;END_TYPE

-subranges

TYPE DataType4 : SINT(0..10);END_TYPE

 

All can be defined as types and then used in variable declarations (interfaces of cats, composites, basics...) or in your symlinks definition

 

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TomRos
TomRos Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-10-13 08:42 AM . Last Modified: ‎2021-10-15 10:36 AM

1 Like
1
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-13 08:42 AM . Last Modified: ‎2021-10-15 10:36 AM

The purpose of POU is to make use of IEC 61131 code.  In order to embed this code inside an IEC 61499 program you should add a PGM block inside the 1499 function block network and trigger the input event from any 1499 function block.  This input will activate the 1131 code.

 

If you have further questions on this topic please let us know.

 

Additionally, we are in the process of reviewing and improving the Help content, so I will bring this feedback into our review.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

anandbpillai
Ensign anandbpillai Ensign
Ensign

Posted: ‎2021-10-27 11:58 PM

0 Likes
1
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-27 11:58 PM

thank you for the reply. @TomRos 

For POU it is ok.

what about Data Type & Function. 

Also as you rightly said the help files needs more update for all of these.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PatrickJouvenel
Crewman PatrickJouvenel Crewman
Crewman

Posted: ‎2021-11-10 06:54 AM

In response to anandbpillai
2 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-10 06:54 AM

for Datatype is quite straightforward:

- enumeration 

TYPE DataType3 : (item1,item2,item3);END_TYPE

- alias

TYPE DataType2 : BOOL; END_TYPE

-struct

TYPE DataType1 : STRUCT 
item1  : BOOL;
item2  : REAL;
item3  : STRING;
 END_STRUCT;
END_TYPE

-array

TYPE DataType5 : ARRAY[0..4] OF BOOL;END_TYPE

-subranges

TYPE DataType4 : SINT(0..10);END_TYPE

 

All can be defined as types and then used in variable declarations (interfaces of cats, composites, basics...) or in your symlinks definition

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JLux
JLux Cadet
Cadet

Posted: ‎2021-11-12 10:34 AM

In response to TomRos
0 Likes
0
2311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-12 10:34 AM

Do you have an example using the PGM Bloc - Cant find it in any existing libraries

 

thx

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.