How to Adjust Scaling for analog input using Ecostruxure Automation Expert
EcoStruxure Automation Expert / IEC 61499 Forum
Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • How to Adjust Scaling for analog input using Ecostruxure Automation Expert
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
Back to EcoStruxure Automation Expert / IEC 61499 Forum
aliffdani
Crewman aliffdani
Crewman
Posted: ‎2025-01-22 05:26 AM
1212
Hi, I have a problem to adjust scaling for analog input. Currently, my EAE connect with Modicon M251. I have Analog Input Module TM3AI8 that connect to plant. I got the line-line value at the plant which is 11kV, but in EAE software, i got different value.
Please help me on how to scale the value to ensure can read in HMI, based on site, minimum is 0kV and maximum is 11kV. The range I used in AI is 4...20mA.
jpb
Ensign jpb Ensign
Ensign
Posted: ‎2025-01-22 10:36 PM
Hi Alif,
To build on the other response, you will need to bring the raw value into the application using a SYMLINK and then process the analog value using either a one of the standard EAE library blocks such as the AiSignalScaling or AnalogueInput CATs or a custom library object.
If using one of the native EAE library components, you can set the scaling parameters using the faceplate as described in the answer from Mohamed, or using offline parameterization as he also mentioned:
Hopefully this helps.
James
mohamedriswan
Ensign
Posted: ‎2025-01-22 08:37 PM
Hi Alif,
You can configure the scaling either from the Offline parameter or the Faceplate parameter. In the Faceplate parameter, adjust the minimum raw value to 4 mA and the maximum raw value to 20 mA. Also, set the PV minimum to 0 kV and the PV maximum to 10 kV. Attached the Faceplate parameter for your reference.
jpb
Ensign jpb Ensign
Ensign
Hi Alif,
James