Establishing an unsecured communication channel with Softdpac on a Ubuntu virtual machine.

EcoStruxure Automation Expert / IEC 61499 Forum

Schneider Electric support forum to acquire and share knowledge about EcoStruxure Automation Expert and IEC 61499 standard for distributed control systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • EcoStruxure Automation Expert / IEC 61499 Forum
  • Establishing an unsecured communication channel with Softdpac on a Ubuntu virtual machine.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
mohamedriswan
Ensign mohamedriswan Ensign
6
KarimBenameur
Ensign KarimBenameur Ensign
4
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Automation Expert / IEC 61499 Forum
Start a Topic
NascimentoOliveira
Crewman NascimentoOliveira
Crewman

Posted: ‎2025-05-15 07:04 AM

0 Likes
4
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-15 07:04 AM

Establishing an unsecured communication channel with Softdpac on a Ubuntu virtual machine.

I'm starting a SofdPAC in an Ubuntu virtual machine. However, I need to create an unsecured communication channel, and I would like to use port 51499 for this purpose. The problem is that I can't find which parameter to modify or the configuration in order to create this channel, since the default setup uses port 51433 and creates a secured channel.

 

The SoftdPAC version is 24.0.24178.

The EAE version used to access the SofdPAC is 24.0

 

NascimentoOliveira_0-1747317233354.pngNascimentoOliveira_1-1747317522097.png

 

Labels
  • Labels:
  • EcoStruxure Automation Expert
  • IEC 61499
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
theo.bagieu
Ensign theo.bagieu Ensign
Ensign

Posted: ‎2025-05-19 12:39 AM . Last Modified: ‎2025-05-19 12:39 AM

0 Likes
1
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 12:39 AM . Last Modified: ‎2025-05-19 12:39 AM

Hi @NascimentoOliveira 

Can you precise which communication you're expecting to be unsecure : Communication between softdpac and Buildtime (EAE Studio Engineering Tool) ? a communication protocol ? Deployement ?

Reply

Link copied. Please paste this link to share this article on your social media post.

NascimentoOliveira
Crewman NascimentoOliveira
Crewman

Posted: ‎2025-05-19 05:01 AM

In response to theo.bagieu
0 Likes
0
696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 05:01 AM

Hi @theo.bagieu.

 

It is a Deployment communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimBenameur
Ensign KarimBenameur Ensign
Ensign

Posted: ‎2025-05-19 09:55 AM

0 Likes
1
722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 09:55 AM

Hi, 

We are not officially supporting unsecure communication but ...you can try that for test purpose only:

- Start manually soft dpac by using startSoftdPAC.sh script

 Note that this will be deprecated soon and it is not recommended to use that script.
- Manage your Soft dPAC docker Linux as a Soft dPAC Windows.
Refer to Soft dPAC user manual following chapters

Configure Soft dPAC for Windows for Non-Secure Communications


I have copy/paste user manual for 24.1

Configure Soft dPAC for Windows for Non-Secure Communications

Soft dPAC for Windows supports only non-secure communications. By default, EcoStruxure Automation Expert - Buildtime configures Soft dPAC controllers for secure communications. Thus, you need to configure each Soft dPAC for Windows controller for non-secure communications.

If you do not configure a Soft dPAC for Windows controller for non-secure communications, it will not be possible to login to the controller from EcoStruxure Automation Expert - Buildtime.

Prerequisites

Before performing the following tasks:

  • Verify that your solution contains the SE.DPAC library reference.

  • Disable the host firewall when performing the following tasks. When the tasks are completed, re-enable the firewall.

1. In the Physical Devices Editor

Configure the host device:

NOTE: When the Soft dPAC manager service is activated, it is not possible to create Soft dPAC runtime services in the Runtimes Editor.
  1. Add a host device - for example a workstation - to the physical devices network.

  2. Select the host device (and not its NIC) to display the Properties tab. (If necessary, select View > General Pads > Properties in the main menu.)

  3. In the Runtimes row, click the ellipsis (...) to open the Runtimes Editor.

  4. Click Add then select Soft dPAC. A new runtime is created and displayed in the right pane.

    NOTE: After the Soft dPAC manager service is activated, It is not possible to create Soft dPAC runtime services in the Runtimes Editor (accessed by clicking the ellipsis (...) at Runtimes Settings > Runtimes).
  5. Click OK to close the Runtimes Editor.

  6. Click on the NIC (i.e. the Ethernet port) on the host device to display its properties.

  7. Configure its Name, IP Address and Logical network properties.
    NOTE: The IP Address is the actual IP address of the host device where the Soft dPAC is running.

2. In the Logical Devices Editor

Configure the security settings of the logical device:

  1. Open the Logical Devices editor in EcoStruxure Automation Expert - Buildtime.

  2. Open the Properties pad ( View > General pads > Properties) if it is not already open.

  3. In the Logical Devices editor, select the Soft dPAC for Windows controller in the list of logical devices to display its properties.

  4. In the Properties pad configure the following settings:

    • Change the Security Settings > Use Encryption setting to False.

      NOTE: A message asks you to confirm changes. Click I confirm to continue.
    • Change the Runtime Configuration > Communication > Endpoint > WebSocket > Encryption setting to False.

      NOTE: A message opens reminding you to edit the Use Encryption setting (which you did, above) and to re-deploy the device configuration. Click OK to continue.
    • Press Ctrl + S (or the main toolbar Save command) to save your changes.

  5. If you have not yet done so, in the Logical Devices editor, associate the Soft dPAC logical device with a Physical Device.

  6. Confirm that the physical device hosting the Soft dPAC is a Windows™ device, which requires a non-secure connection, and not a device (e.g., a Linux device) that supports only secure connections.

  7. In the Deploy and Diagnostic pad, you can now proceed to Compile, Login to the device, and Deploy the device configuration.

  8. Once deployed, if no OPC UA communication can be established, confirm that the real physical device is configured with an unsecure connection for OPC UA.

3. In the Deploy and Diagnostic Editor

Deploy and run the Soft dPAC:

  1. Select Action > Login.

  2. After login, select Action > Compile.

  3. Once compiled, select Action > Device configuration > Deploy Device Configuration. The Deploy Device Settings dialog opens, presenting the options:

    • Deploy and Restart

    • Deploy only

    • Cancel

  4. Select Deploy and Restart.

  5. After all device configuration is complete, deploy the configuration to runtime by selecting Action > Deploy > Deploy.

  6. After deploy is complete, you can run the device by selecting Action > Device action > Run.

    The Soft dPAC runs in unsecured mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

NascimentoOliveira
Crewman NascimentoOliveira
Crewman

Posted: ‎2025-05-19 12:03 PM

In response to KarimBenameur
0 Likes
0
696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 12:03 PM

When I try to initiate a sofdPAC by running  startSoftdPAC.sh, I received this error message: 

NascimentoOliveira_0-1747681259191.png

 

However, I configured the daemon file as this installation note demands:

NascimentoOliveira_1-1747681332614.png

NascimentoOliveira_2-1747681387500.png

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore