Struggling all day trying to get Ecostruxure operator terminal Expert simulation to read symbols/data from a live PLC
I have set up the symbol link ok in the M241 and have no errors reported on the Ecostruxure operator terminal Expert
Any ideas?
Best Regards
Dave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 04:23 AM
Did the problem ocur only in simulation or also on a real HMI? I would suggest the ethernet Settings are the problem. In simulation your PC works as SoftHMI. The IP of you PC and the PLC must match in that case.