Uniflair DDF identification guide for Data Center Expert

DCE FAQ

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Data Center Expert
  • DCE FAQ
  • Uniflair DDF identification guide for Data Center Expert
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to DCE FAQ
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2245 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Uniflair DDF identification guide for Data Center Expert

Picard EcoStruxureIT
‎2019-11-20 06:15 AM

This table will help you accurately identify the appropriate DDF for any Uniflair model.

Only one Carel pCOWeb SNMP DDF can be installed per DCE server regardless of vendor.

See Carel pCOWeb cards for more information.

NOTE: An asterisk (*) in the Device Family/SKU name indicates a wildcard value, for example, TRAF1221A1 and TRAC4042A1 would both fall under "TR******A (last letter is A).

NOTE: pCO5 and pCO5+ are different controllers.

Modbus

File Name Device Family/SKU Controller/Interface
uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU

 

pCO1/UG40
 

Uniflair LE: TDCR, TUCR, TDCV, TUCV, IDAV, TDAR, TDDR, TDDV, TDER, TDTR,

TDTV, TDWR, TUAR, TUDR, TUDV, TUER, TUTR, TUTV, TUWR, TDAV, TDEV, TDWV, TUAV, TUEV, TUWV

Uniflair AM: SDA, SDC, SDW, SUA, SUC, SUW

 

uniflair_am_uniflair_le_amico_leonardo_ug50_TCPIP_Modbus_CCU

 

pCO5+/UG50

 

Uniflair LE: HDCV, HDCV5000D, HDCV5000L

 
uniflair_aquacentr_TCPIP_Modbus_chiller_imperial (imperial units only)

BCE*, BCW*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5+/UG50
uniflair_aquascrew_TCPIP_Modbus_chiller

BRE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5+/UG50
uniflair_aquascroll_TCPIP_Modbus_chiller

ERAC, ERAH, ERAF, ERCC, ERCH, ERCF

ISAC, ISAH, ISAF, ISCC, ISCH, ISCF

TR******A (last letter is A)

NOTE: Aquascroll Firmware

pCO5+/UG50
uniflair_aranew_TCPIP_Modbus_chiller ARAC, ARAH, ARAF pCO1/MP20II
uniflair_bce_TCPIP_Modbus_chiller

BCE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5/UG50
uniflair_bcwc_TCPIP_Modbus_chiller

BCW*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO3/UG50
uniflair_bra_TCPIP_Modbus_chiller BRA* pCO1/MP20II
uniflair_bref_TCPIP_Modbus_chiller

BRE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match.

pCO1/MP20II
uniflair_brwc_TCPIP_Modbus_chiller BRR*, BRW* pCO1/MP20II
uniflair_era_TCPIP_Modbus_chiller

ERAC, ERAH, ERAF, ERCC, ERCH, ERCF

NOTE: pCO controller and firmware determine the correct DDF to use. They MUST match.

NOTE: Does NOT use Aquascroll Firmware

pCO1/MP20II
uniflair_isa_TCPIP_Modbus_chiller

ISAC, ISAH, ISAF, ISCC, ISCH, ISCF

NOTE: pCO controller and firmware determine the correct DDF to use. They MUST match.

NOTE: Does NOT use Aquascroll Firmware

pCO1/MP20II
uniflair_lra_TCPIP_Modbus_chiller LRAC, LRAH pCOXS/-
uniflair_sp_uniflair_wm_uniflair_mb_telnew_TCPIP_Modbus_CCU

UCA* , UCF*, UWA*, UWF*,WDA*, WDF*, WMA*, WMF*,XDA* , XDF*, (ADD*/ XDD* displacement units), XMA*, XMF*

pCO1/UG40
uniflair_tra_TCPIP_Modbus_chiller

TR******A (last letter is A)

NOTE: TRA 1.x Firmware

pCO5+/UG50

 

SNMP

NOTE: Any file name with a leading asterisk (*) is included with a DCE installation.

NOTE: File names that are bold are considered pCOWeb SNMP DDFs as mentioned at the top of this article. 

File Name Device Family/SKU Controller/Interface
*apc_acrd2g ACRC60xx, ACRD60x Schneider C3P (R2)/Touch (4.3")
apc_air_economizer

IAEC25, IAEC50

Schneider J5-18DIN/Touch (7")
*apcacirg2 ACRD10x, ACRD20x Schneider C3P (mR1)/PowerView
*apcacsc ACSC10x Schneider C3P (mR1)/PowerView
*apcraru ACF40x Schneider ARU (mR1)/PowerView
*schneider_acrc301s ACRC30xx Schneider J5-13DIN/Touch (4.3")
*schneiderelectric_ledxg2 LD*V* / IX*V* / I**V* Schneider J5-18DIN/Touch (7")
schneiderelectric_tsatra TSA*, TR******A1 (last characters are A1) pCO5+/Touch (7")
uniflair_am_uniflair_le_amico_leonardo_ug40mp40_SNMP_CCU

Uniflair LE: TDCR, TUCR, TDCV, TUCV, IDAV, TDAR, TDDR, TDDV, TDER, TDTR,

TDTV, TDWR, TUAR, TUDR, TUDV, TUER, TUTR, TUTV, TUWR, TDAV, TDEV, TDWV, TUAV, TUEV, TUWV

Uniflair AM: SDA, SDC, SDW, SUA, SUC, SUW

pCO1/UG40
uniflair_am_uniflair_le_amico_leonardo_ug50mp50_SNMP_CCU

Uniflair LE: HDCV, HDCV5000D, HDCV5000L

pCO5+/UG50
uniflair_aquacentr_SNMP_chiller_imperial (imperial units only)

BCE*, BCW*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5+/UG50
uniflair_aquascrew_SNMP_chiller

BRE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5+/UG50
uniflair_aquascroll_SNMP_chiller

ERAC, ERAH, ERAF, ERCC, ERCH, ERCF

ISAC, ISAH, ISAF, ISCC, ISCH, ISCF

TR******A (last letter is A)

NOTE: Aquascroll Firmware

pCO5+/UG50
uniflair_aranew_SNMP_chiller ARAC, ARAH, ARAF pCO1/MP20II
uniflair_bce_SNMP_chiller (metric units only)

BCE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5/UG50
uniflair_bra_SNMP_chiller BRA* pCO1/MP20II
uniflair_bref_SNMP_chiller

BRE*

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO1/MP20II
uniflair_brwc_SNMP_chiller BRR*, BRW* pCO1/MP20II
uniflair_era_SNMP_chiller

ERAC, ERAH, ERAF, ERCC, ERCH, ERCF

NOTE: pCO controller and firmware determine the correct DDF to use. They MUST match

NOTE: Does NOT use Aquascroll Firmware

pCO1/MP20II
uniflair_isa_SNMP_chiller

ISAC, ISAH, ISAF, ISCC, ISCH, ISCF

NOTE: pCO controller and firmware determine the correct DDF to use. They MUST match

NOTE: Does NOT use Aquascroll Firmware

pCO1/MP20II
*uniflair_le_ddf

T*C* (third letter "C")

HDCV*

T*AG, T*DG, T*WG, T*TG, T*EG, (last letter G)

NOTE: pCO controller determines the correct DDF to use. Controller MUST match

pCO5+/Touch (7")
Uniflair_LEL LDCV* pCO5+/Touch (7")
uniflair_lra_SNMP_chiller LRAC, LRAH pCOXS/-
uniflair_sp_uniflair_wm_uniflair_mb_telnew_SNMP_CCU UCA* , UCF*, UWA*, UWF*,WDA*, WDF*, WMA*, WMF*,XDA* , XDF*, (ADD*/ XDD* displacement units), XMA*, XMF* pCO1/UG40
uniflair_trac_SNMP_chiller

TR******A (last letter is A)

NOTE: TRA 1.x Firmware

pCO5+/UG50
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of