New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Carel pCOWeb cards
DCE FAQ
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Some devices, including many Uniflair cooling devices, use a network card from Carel called pCOWeb.
These cards can be problematic for Data Center Expert because the type of device they are installed in is not identified, and the same SNMP addresses (OIDs) are used to represent different things.
DCE cannot automatically choose the correct DDF for devices with pCOWeb network cards.
If you only have one DDF installed to support devices that use the pCOWeb card, it's not a problem.
If you need multiple DDFs to support devices that use the pCOWeb card, you must configure the card to provide identifying information and modify the DDF to look for that information.
To configure the pCOWeb card:
Follow the instructions on page 35 of the pCOWeb User Manual to change the value of the system name at OID 1.3.6.1.2.1.1.5. The name should identify the DDF to use, for example, amico_leonardo_ug40mp40.
To modify the DDF:
Open the DDF in a text editor and find this line (note that the xxxxxx will vary between DDFs: