xPBA4 & xPBD4 Expansion Module Compatibility
  • xPBA4 & xPBD4 Expansion Module Compatibility
‎2018-09-10 01:30 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:04 AM
Can the xPBD4 be used with an i2 or b3.
xp Expansion Module
Is the xPBD4 compatible with an i2 or b3.
No. The following note is from the xP Expansion Datasheet:
The xPBA4 and xPBD4 Expansion Modules can only be connected to the bCX1 Controller/Routers and ACX Series Access Controllers.
The other xP expansion modules do work with the i2/b3 controllers. See the attached data sheet for more info.
  • 11476