What is the "meter factor", what does it mean?
Kamstrup
Heating meter
cooling meter
flow meter
Multical
601
602
The "meter factor" is mentioned in the documentation, but what does it mean?
The "meter factor" is the number of impulses/Liter, and differs between the different sizes of meters. This value is described in the data sheet. The meter factor can also be seen on the label on the side of the meter.