"TrendLogWizProfiles not found" error when trying to create a trend log
  • "TrendLogWizProfiles not found" error when trying to create a trend log
  • SESA116857
    SESA116857
‎2018-09-06 02:59 PM
Vista Workstation
Trend Log
This error can be caused when the Trend Log wizard profiles file has become corrupted.
  1. Browse to the TAC Vista directory in Vista Workstation
  2. Double click on the $TrendLogWizProfiles object.
  3. At the bottom is the "Source File Name". Click on the data field and click the browse button "...".
  4. Browse on your hard drive to $ini directory found in the Vista Installation directory (C:\Program Files\TAC\TAC Vista 4.5.0\$ini for Vista 4.5.0).
  5. Select the $TrendlogWizProfiles.xml file and click "Open" and then "Ok".
  6. The profiles should now be updated and you should be able to use the create trend log wizard again.
  • 2538