Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

"Out of memory" warning dialogue window pops up when trying to access objects in Vista.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Out of memory" warning dialogue window pops up when trying to access objects in Vista.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1330 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Out of memory" warning dialogue window pops up when trying to access objects in Vista.

Picard Product_Support
‎2018-09-10 01:27 AM

Issue

  • "Out of memory" warning dialogue window pops up when trying to access objects in Vista.
  • How to create a performance log to monitor Vista's memory usage

Environment

All Operating Systems

TAC Vista 5.1.X - server and workstation

Cause

Memory usages exceeds the allocated memory on the PC.

Resolution

  1. Check the memory usage.
    1. The first step is to simply check the memory usage of all the processes that are running. Open task manager (right-click on the task bar and select from the context menu).
    2. Select the tab Processes and check that there are no processes using a large amount of memory. Especially interesting are TACOS.exe (Vista server) and TACVistaExplorer.exe (Vista Workstation).
  2. If everything looks OK here monitor Vista's memory usage.
    1. Click on Start->Run and type in perfmon. Click on OK.
    2. Select System Monitor in the menu-tree to the left.
    3. Click on the + (plus) symbol in the graph pane to the right.
    4. Use the following settings:
       
    5. Click add and then do the same adding TACVistaExplorer.
    6. In the same way add Memory - Available bytes
    7. Monitor the memory usage and check to see if anything unusual happens - if TACOS's memory usage is near the available bytes or if TACOS's memory usage keeps growing etc.
  3. If it's possible to establish that TACOS and TACVistaExplorer are using a large percentage of the PC's memory, upgrade to Vista 5.1.6. and/or increase the physical RAM of the PC (if possible).
    A lot of improvements have been made to TAC Vista that have optimized memory usage. A significant reduction in memory usage should occur after upgrade.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6004
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of