Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

"No communications adapter found. Comm error = -5" connecting XPSI 4.1 to MicroZone II using B&B USOPTL4 converter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "No communications adapter found. Comm error = -5" connecting XPSI 4.1 to MicroZone II using B&B USOPTL4 converter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2071 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"No communications adapter found. Comm error = -5" connecting XPSI 4.1 to MicroZone II using B&B USOPTL4 converter

Picard Product_Support
‎2018-09-06 01:15 PM

Issue

When trying to connect XPSI version 4.1 to a MicroZone II, using a B&B Electronics converter, model USOPTL4,
an error is received: "No communications adapter found. Comm error = -5".
Online XPSI functions may be grayed-out and not available:

Environment

XPSI version 4.1

USB / RS-485 adapter, B&B Electronics model USOPTL4

Network 8000 MicroZone II controller

Cause

One cause of the error appears to be closing the XPSI Site Group window:

Resolution

Leave the Site Group window open.

Edit the Site setup. In the following example, the site is named "B&B converter to MZ2".

To communicate to a stand-alone MicroZone II, the Network Number and GCM Number do not matter, they can be left at their default values.

The "Connection Type" should be set to PSI HOST

 

The "Port" should be set to match the hardware port assigned to the B&B converter when installing its drivers. It will be named
" RS-485 Isolated Port (COMx)". COM3 in the following example. Note the Universal Serial Bus Controllers, Model USOPTL4.

Once the site is configured, access the controller:

Enter the user name and password for the MicroZone II on the MicroZone II PSI Main Window:

 

In the "Functions" menu, use the arrow keys to move the cursor to "Device Number", and press "Enter".

Type in the address of the controller, which is set by its DIP switch. The MZ2 is set to address = 1 in the example:

While XPSI is connecting to the MZ2, the TD and RD LEDs on the model USOPTL4 should blink. 
The  yellow (RX) and green (TX) LEDs on the MicroZone II should also blink.

When XPSI is connected to the controller, the Main Window will display the device number. In the example, MZ II # 001 is connected:

When finished accessing the MicroZone II, logoff and select "Disconnect" from the Access menu. This will properly shut down XPSI and the drivers for the B&B converter.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6435
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore