Issue
"Invalid attribute property" error when trying to create NetController II in Continuum v1.74 SP2 as Controller Type "9681".
Environment
Continuum v1.74 SP2
NetController II
Cause
Trying to create new NetController II device object with a "Controller Type" of "9681".
"A Guide to Version 1.74 Support for NetController II and ACX 57xx" states that there is only one NetController model, the CX 9680. Please ignore references to the 9681.
Resolution
Create the Netcontroller II as a Controller Type "9680" as stated on page 15 in document number 30-3001-1001 "A Guide to Version 1.74 Support for NetController II and ACX 57xx".