"Failed to Initialize Necessary Resources" error message when opening ZBuilder: XIF file
  • "Failed to Initialize Necessary Resources" error message when opening ZBuilder: XIF file
  • SESA116857
    SESA116857
‎2018-09-06 02:48 PM
  • Xenta 121
  • ZBuilder
One way this error message can occur is if a Xenta 121 device has been added, but not associated with an XIF file.
If this is a classic network, then you can browse to the C:\Program Files\TAC\TAC Vista x.x.x\$ini\ directory to find the XIF file which corresponds to the 121 you are using (HP or FC).
In an LNS system you should check the template of the device to make sure it has the proper XIF file associated with the template.
  • 3039