"Error 1311 source file not found" when installing Cyberstation base on webClient
  • "Error 1311 source file not found" when installing Cyberstation base on webClient
  • YangboLIU
    YangboLIU
‎2018-09-06 12:23 PM
When upgrading Continuum Cyberstation to a higher version on a webClient machine without uninstalling webClient first, the installation will not be successful.
Error 1311, Source file not found, pls verify the file "....\Cyberstation1.94\continuum\webcli~1.cab" existed and can access it.
  • Windows XP SP3
  • webClient 1.93
  • Cyberstation 1.94
The webClient was not uninstalled successfully. The Cyberstation install process interprets the installation as an upgrade and tries to find the webClient install file "webcli~.cable." When the file is not found in the Continuum folder, the error is encountered.
  1. Uninstall Webclient and delete Continuum folder from the machine
    1. From Windows Control Panel, click "add/remove program" and find  "Continuum" then click.
    2. Click "yes" button from the pop-up alarm dialogue window.
    3. After uninstallation finished, go to  C:\program files\continuum, and then delete the whole folder.
  2. Restart the machine
  3. Re-Install Cyberstation
  • 7870