Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

"Cannot paste. /tridium/props/error.properties#error.E_RC_TO_NODE" when trying to paste a Lon shadow object into the workspace of an UNC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Cannot paste. /tridium/props/error.properties#error.E_RC_TO_NODE" when trying to paste a Lon shadow object into the workspac...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1532 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Cannot paste. /tridium/props/error.properties#error.E_RC_TO_NODE" when trying to paste a Lon shadow object into the workspace of an UNC.

Picard Product_Support
‎2018-09-06 12:42 PM

Issue

"Cannot paste. /tridium/props/error.properties#error.E_RC_TO_NODE" when trying to paste a Lon shadow object into the workspace of an UNC.

Environment

  • Niagara R2
  • UNC-410
  • UNC-520

Cause

There could be two possible causes for the error message. One possible cause is that the Lon jar file which contains the shadow object was updated on the WorkPlace Pro PC, but the updated module was never installed to the UNC. The other possible cause is that the updated Lon nt jar file was not installed in the \nre\modules folder of the WorkPlace Pro PC.

Resolution

There are two things to look into. Perform both procedures 1 and 2 only if the lon nt jar was not installed/upgraded to the nre\module folder.  If all of the Lon jars are installed/upgraded correctly (Lon nt jar file installed to nre\modules folder) on the WorkPlace Pro PC, then only procedure 2 needs to be performed.

Procedure 1
If the lon nt file was not installed/updated to the \nre\modules folder, use the following steps to do so. These steps assume that the updated Lon nt jar is already installed on the WorkPlace Pro PC, but not it was not installed to the nre\modules folder.

  1. Stop WorkPlace Pro.
  2. Open the Niagara\build\nt and copy the Lon jar
  3. Open the niagara\build\nre\module folder and rename the Lon jar in question “.old”.
  4. Paste the copied Lon jar to the module folder and restart WorkPlace Pro.

The module will now need to be upgraded to the UNC. See above steps for procedure.

Procedure 2
If the UNC Lon module has not been installed/updated to the UNC, use the following steps to do so.

  1. Open the Admin Tool.
  2. Open a connection to the UNC
  3. Select the "Installation" tab then click the [Installation Wizard] button.
  4. Select the "emb" folder in the "Select Distribution Directory" window then click [Install]
  5. In the "Niagara Remote Installation" window, select the "Configure Modules Only" radio button then click the [Next >] button.
  6. Verify that there is a checkmark in the "Upgrade/Add" column for the updated lon jar file.
  7. Click the [Next >] button to continue. Make sure that on the "Database Backup" screen that you do backup the existing database.
  8. Continue through the remaining steps and allow the upgrade to install and the station to restart.

You should now be able to paste the shadow object to the WorkspaceEditor view.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7278
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore