When starting I/NET from filemaster PC, why do I receive an error message that states "cannot equalize with filemaster?"
I/NET Site
Verify that the PC name of the filemaster has not changed. You can do this within the Configuration profile by deselecting/reselecting the filemaster checkbox.
If the PC name change is discovered:
  1. Shut down I/NET, I/O Server, Equalsrv, and Equalcli.
  2. Go into Windows Explorer and delete all *.hfg files.
  3. Reboot PC
  4. Start I/NET