Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

"BACnet" Extended Trend Logs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "BACnet" Extended Trend Logs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3776 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"BACnet" Extended Trend Logs

Picard Product_Support
‎2018-09-11 01:20 AM

Issue

Extended Trend Logs

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server Premium (AS-P)
  • Building Operation Automation Server Bundled (AS-B)

Cause

When configuring extended logging in the BACnet application folder, these objects are not available when performing a device discovery from the AS or ES.

  1. Prepare one AS with a BACnet point
  2. Create a trend log on the BACnet point
  3. Create an Extended log for that BACnet trend log

From a second AS, the BACnet objects are available after a Device Discovery except for the Extended log object.

StruxureWare Building Operation online help for “Configuring Extended Logging for a BACnet Trend Log” states: 

 

***Key Concept: Extended trend logs are not BACnet objects. These are StruxureWare Building Operation exclusive. The term "BACnet Extended Trend Log" does not exist and is a misnomer.

Resolution

The main reason is that extended logs are not defined in the BACnet standard; they are proprietary to EcoStruxure. 

Everything that is proprietary to EcoStruxure Building Operation is not exposed to BACnet including graphics, script & function block programs and central IO points are not directly exposed, but have to be bound to BACnet I/O objects.

The extended log serves the purpose of expanding a log on a larger capacity server.  A trend log on an AS would be more appropriate to extend on an ES. If you have a trend log in an external BACnet device (like a b3 or a 3rd party device/system) then you would want an extended log in the AS, to collect from that device (and then maybe a larger extended trend on a parent ES).


If there is a local BACnet trend log in an AS (in the BACnet interface application folder) that is required to be larger, consider increasing the buffer size property of the one log that is needed (the default size of 10 may be too small, and increasing to 1000 up to 5000 (extended log size) may be an option). That would be most interoperable with other (3rd party) BACnet clients that need access to the trend log data.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 12882
  • DavidChild20
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore