Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

java.lang.Security Exception:: class "WbApplet does not match trust level of other classes in the same package"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • java.lang.Security Exception:: class "WbApplet does not match trust level of other classes in the same package"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3050 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

java.lang.Security Exception:: class "WbApplet does not match trust level of other classes in the same package"

Picard Product_Support
‎2018-09-06 11:44 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:30 AM

Issue

On December 13, 2012, the certificate verifying the authenticity of the Schneider Electric I/A Series G3 Workbench Applet (wbapplet) expired. Users will see the following error in their browser when accessing a station that is using a version of the wbapplet.jar with an expired code signing certificate:

Environment

Niagara G3

Cause

When accessing an I/A Series G3 station through a web browser using a WbWebProfile, the web browser runs Workbench within a Java applet. To enhance security, this applet is 'signed' using a code signing certificate. This ensures that the applet has come from a reliable source and can be trusted to run with the proper permissions.

Certificates used to sign applets are issued by a Certificate Authority (CA). Each code signing certificate issued by a CA has an established expiration date, with the maximum expiration being two years. Once this expiration date has passed, continuing to use a Java applet with an invalid certificate will result in warning messages within the browser. The applet will only be allowed to run after the user has acknowledged the warning and granted approval.

Resolution

An updated certificate is available in the new wbapplet.jar, available from The Exchange Download Center. This file will need to be added to the Enterprise Network Server, as well as on any ENCs that will be accessed from a browser.

This file is for all released versions of TAC I/A Series G3 and is valid until March 30, 2015. Download wbapplet_March_2015.zip. Extract the wbapplet jar file  Click and Download The WbApplet Installation Guide. Note: Updated WbApplet files are available as part of upcoming Niagara 3.5 and 3.6 maintenance builds, as well as being from the Source website. In 3.7, wbapplet.jar is integral to the web.jar and contains an up to date certificate.;

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 12127
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore