b3 to b3 and i2 Infinet Binding Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • b3 to b3 and i2 Infinet Binding Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4227 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

b3 to b3 and i2 Infinet Binding Operation

Picard Product_Support
‎2018-09-06 07:40 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:57 AM

Issue

What binding methods can be used and how is the data transferred when binding objects between two b3  or Infinet controllers?

Product Line

EcoStruxure Building Operation

Environment

  • Automation Server, AS, ASP, ASB
  • BACnet b3
  • Infinet controllers i2

Cause

When binding objects between b3(infinet) devices/controllers, the type of Objects being bound will effect the properties of the binding.

Resolution

When binding between two Controllers, several methods can be used:

  • Value/Point to Value/Point - The data goes via the Automation Server and the speed/rate is set in the Transfer Window, thus more bandwidth used and communication is lost if the Automation Server fails.
  • Script to Value/Point - The data goes direct using BACnet COV subscriptions, thus less bandwidth is used.

NOTE - The BACnet b3 and Infinet controllers, have no facility for direct binding of Value/Point to Value/Point, thus if a direct binding is made within the same controller, an EBO binding will be created. This will cause data packets on the MSTP or Infinet network. This should usually be avoided, as it can easily overwhelm the network. Bindings should usually be made from scripts.

See Infinet under the hood for more details on Infinet setup

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (10)
  • Find more articles tagged with:
  • 19028
  • as
  • asb
  • asp
  • b3
  • bacnet
  • binding
  • DavidShore20
  • i2
  • infinet
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore