Xenta server stand alone and Vista at the same time
  • Xenta server stand alone and Vista at the same time
  • Benji
    Benji
  • sesa150555
    sesa150555
‎2018-09-06 01:05 PM
  • Xenta server stand alone and Vista at the same time.
  • No alarms showing in TAC Vista when Xenta Server is connected.
TAC Vista
TAC Xenta Server
If you add a stand alone Xenta Server on a Lon network it will send out heartbeats just like TAC Vista does.
So the affect will be the same as having 2 TAC Vista servers on the same network.  But there is a way to turn this off.
In Xbuilder you can turn this off by setting "Alarm Server" to disabled
  1. In Xbuilder click on the LON object
  2. Under General properties change "Alarm Server" to disabled.
  3. Download the project.
  • 6584