Issue
The TAC Xenta Operator Panel does not hold steady when navigating down into programmable controller point lists. At random times the OP will back out and return to the main screen with the list of programmable controllers.
Environment
- Operator Panel (OP)
- Vista
Cause
The XENTASYSREG bit 0 does not work in version 3.87 of the Xenta programmable controllers.
Resolution
The latest firmware hotfixes need to be downloaded and installed for the corresponding TAC Xenta programmable controllers. For all Xenta Versions, download Hotfix version 3.87-02 on The Exchange Download Center.