When checking the error log of an Xenta there is a error "NoLink 29". The error means that the network cable has been unplugged or that the Xenta has lost contact with the host in another way.
1. Check so that there is no loose ends on the TCP/IP cable connected to the Xenta and the router/switch.
2. Check with IT department to see if there has been any planned or unplanned disruption on the network.