Xenta Servers and Time Synchronization

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta Servers and Time Synchronization
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3316 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta Servers and Time Synchronization

Picard Product_Support
‎2018-09-07 01:49 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:57 AM

Issue

The time in TAC Xenta Server should be the same as the time on the TAC Vista Server PC.

When Xenta Servers connect to the TAC Vista Server, they should synchronize their time with the Vista PC.

Product Line

TAC Vista

Environment

  • Xenta Servers
  • Xenta 511, 527, 701, 711, 721, 731, 913
  • NTP Server
  • Vista Server

Cause

There are different scenarios.

  1. Vista Server PC has no internet connection
  2. Vista Server PC has internet connection

Resolution

Corresponding to the causes above:

  1. Set the Xenta Server to synchronize with the Vista Server PC. You do that by adding this AuthoritativeNTPserver.zip reg file to the registry on the TAC Vista Server PC, and enter the IP address of the PC into the Xenta Server as described in Setting NTP in Xenta Server.pdf.
  2. Set the Xenta Server and the Vista Server PC to synchronize with a NTP server on the internet. Find servers here: http://support.ntp.org/bin/view/Servers/NTPPoolServers
    Area HostName
    Worldwide pool.ntp.org
    Asia asia.pool.ntp.org
    Europe europe.pool.ntp.org
    North America north-america.pool.ntp.org
    Oceania oceania.pool.ntp.org
    South America south-america.pool.ntp.org

In general, make sure that firewall is not an issue. NTP uses port UDP 123

Labels (1)
Labels:
  • TAC Vista
Attachments
AuthoritativeNTPserver.zip
Tags (6)
  • Find more articles tagged with:
  • 3224
  • network
  • protocol
  • sntp
  • synchronized
  • windows
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore