Xenta Server wiring guide and description table
  • Xenta Server wiring guide and description table
  • SESA128463
    SESA128463
‎2018-09-10 07:56 AM
The need to verify the proper wire positions on a Xenta Server device
  • Vista
  • XBuilder
  • Xenta Servers
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913
Installing a Xenta Server device on a network
Table 2.1: Connections on the Xenta device
Position Description
1-2 Power supply. Minimum cross-sectional area 0.75 mm2 (AWG-19).
  • 1 (G) - 24 V AC (or DC+)
  • 2 (G0) - Ground
3-4 LonWorks TP/FT-10 connection
  • 3 (C1)
  • 4 (C2)
5-8 Internal port A RS-485 A connection
  • 5 (RX/TX+)
  • 6 (RX/TX-)
  • 7 (RX+)
  • 8 (RX-)
Note that the interface RS-232 A (position 21) and interface RS-485 A (position 5-8) are internally connected to port A on the processor. Only one should be connected.
9 Ground
  • 9 (G0)
10 Fail-safe
Note Jumping these pins together while cycling power will flash the device and load the minimum amount of drivers necessary for communication. If an IP address has already been assigned fail-safe will NOT remove it.
11-15 Unused
16-17 Ground
  • 16 (G0)
  • 17 (G0)
18 Unused
19-20 Internal port C RS-485 C (SDLC) connection
  • 19 (RX/TX+)
  • 20 (RX/TX-)
21 Internal port A RS-232 A connection.
22 Internal port B RS-232 B console connection
23 Ethernet 10Base-T connection
24 Service pin
Caution
  • G0 equals GROUND.
  • Only G0 may be connected to protective ground.
Labels (2)
  • TAC INET
Tags (3)
  • 8066
  • wiring guide
  • xenta server