Issue
The need to verify the proper wire positions on a Xenta Server device
Environment
- Vista
- XBuilder
- Xenta Servers
- Xenta 511, 527, 555, 701, 711, 721, 731, 913
Cause
Installing a Xenta Server device on a network
Resolution
Table 2.1: Connections on the Xenta device
Position | Description |
1-2 | Power supply. Minimum cross-sectional area 0.75 mm2 (AWG-19).
|
3-4 | LonWorks TP/FT-10 connection
|
5-8 | Internal port A RS-485 A connection
|
9 | Ground
|
10 | Fail-safe Note Jumping these pins together while cycling power will flash the device and load the minimum amount of drivers necessary for communication. If an IP address has already been assigned fail-safe will NOT remove it. |
11-15 | Unused |
16-17 | Ground
|
18 | Unused |
19-20 | Internal port C RS-485 C (SDLC) connection
|
21 | Internal port A RS-232 A connection. Note that the interface RS-232 A (position 21) and interface RS-485 A (position 5-8) are internally connected to port A on the processor. Only one should be connected. |
22 | Internal port B RS-232 B console connection |
23 | Ethernet 10Base-T connection |
24 | Service pin |
Caution
- G0 equals GROUND.
- Only G0 may be connected to protective ground.