Xenta Server trend log page only displays the name for one of the Y-Axis even though two have been defined
  • Xenta Server trend log page only displays the name for one of the Y-Axis even though two have been defined
  • sesa150555
    sesa150555
‎2018-09-06 02:37 PM
In trend log page in Xenta Server I only see the name for one of the Y-Axis even though I have defined the name and range for both Y1 and Y2
  • Xenta Server
  • Xenta 511, 527, 711, 731
  • Trend Chart
If you want to display both Y-Axes 1 and 2 you have to have at least 2 logs in the chart.
To see the 2nd Y-Axis you have to use it. Select the log that you want to use the 2nd Y-Axis and change the Display settings.
Tags (3)
  • 3464
  • primary
  • secondary