Issue
Xenta Server is marked with an asterisk and says "Needs to be Commissioned"
Environment
- Vista Workstation
- Xenta Server
- Xenta 511, 527, 555, 701, 711, 721, 731, 913
Cause
The files in the Xenta Server do not match the Xbuilder project stored in the Vista Database.
Resolution
- Right-click on the Xenta Server in Vista Workstation and select Edit. This will open XBuilder.
- In Xbuilder, click "Send to Target" to download the files to the Xenta Server.