  • TGML Graphic does not display. Shows only a red X
  • Xenta Server TGML Graphics not updating following XBuilder download
  • Miscellaneous Java error messages
TAC Vista
  • Xenta 511, 527, 711, 731
  • TGML graphics
  • XBuilder
Dynamic TGML graphics are rendered in the web browser using a Java applet. Java on the PC will store applets and graphics in its cache for faster load times. This can sometimes be problematic as changes are being made -- either to the graphic source files or the firmware version of the Xenta Server.
Clear the Java cache before loading the page again:
  1. Open the Java Control Panel
    • If viewing a Java page, the icon for the control panel will be in the task bar of the PC. Double click it.
    • Otherwise, go to Start > Control Panel > Java.
  2. On the first tab, General, see the third box item, Temporary Internet Files.
  3. Click Settings...
  4. Click Delete Files...
  5. Select both "Applications and Applets" and "Trace and Log Files". Click OK, and exit the Java Control Panel
  6. Reload the graphic.