Issue
When using a web browser to change the SMTP port number from 25 to, for example 465, and save, if leaving the page and navigate back to that page, the changed port number reverts back to 25.
Environment
Xenta 555
Cause
When using a web browser to change the SMTP port number from 25 to, for example 465, and save, if leaving the page and navigate back to that page, the changed port number reverts back to 25.
Resolution
Change the port number to something other than 25 in the Xbuilder project then upload the Xenta's project again.
To:
Now, in the future, you will be able to change the SMTP port number using a browser, if changes are required.