Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Xenta 527 error message "Packet no match on SeqChain type: 2" in HyperTerminal

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta 527 error message "Packet no match on SeqChain type: 2" in HyperTerminal
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1476 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta 527 error message "Packet no match on SeqChain type: 2" in HyperTerminal

Picard Product_Support
‎2018-09-06 01:20 PM

Issue

Xenta 527 showing error message "Packet no match on SeqChain type: 2" in HyperTerminal

Environment

  • I/NET
  • HyperTerminal
  • TelNet
  • Xenta 527

Cause

This error has been added as a means to aid in troubleshooting.  The specific Build of the Xenta 527 system program will change the meaning of this error.

 

  • In 5.1.6 the error indicates a request to the reference hosts for an updated routing table
  •  

     

     

    Resolution

    5.1.5

    1. Contact the local IT department to find possible causes of corrupted IP packets
    2. You may need to use an ethernet capture device to determine the source of the corrupted packets

    5.1.6

    1. If the error is occurring only rarely it can be ignored. 
    2. You may see an increase in error traffic if there is a problem with TCP/IP communication
    3. Contact Product Support if further assistance is required
    Labels (1)
    Labels:
    • TAC INET
    Tags (3)
    • Find more articles tagged with:
    • 6087
    • IP Packet
    • Xenta 527 error
    Was this article helpful? Yes No
    No ratings

    Link copied. Please paste this link to share this article on your social media post.

    You’ve reached the end of your document

    WHAT’S NEXT?

    Ask our Experts

    Didn't find what you are looking for? Ask our experts!

    My Dashboard

    Check out the new Feeds and activities that are relevant to you.

    To The Top!

    Forums

    • APC UPS Data Center Backup Solutions
    • EcoStruxure IT
    • EcoStruxure Geo SCADA Expert
    • Metering & Power Quality
    • Schneider Electric Wiser

    Knowledge Center

    Events & webinars

    Ideas

    Blogs

    Get Started

    • Ask the Community
    • Community Guidelines
    • Community User Guide
    • How-To & Best Practice
    • Experts Leaderboard
    • Contact Support

      Ask our Experts

      Have a question related to our products, solutions or services? Get quick support on community Forums

      Email Us

      For Community platform-related support, please email us

    Brand-Logo
    Subscribing is a smart move!
    You can subscribe to this board after you log in or create your free account.
    Forum-Icon

    Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

    Register today for FREE

    Register Now

    Already have an account? Login

    Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

    Welcome!

    Welcome to your new personalized space.

    of

    Explore