Xenta 121-FC fan runs in cool mode even though cool mode is not used
  • Xenta 121-FC fan runs in cool mode even though cool mode is not used
  • Anonymous user
‎2018-09-06 02:48 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-05-28 06:52 AM
Xenta 121-FC fan runs in cool mode even though cool mode is not used.
TAC Vista
  • ZBuilder
  • Xenta 121
Previous settings configure the cooling in such a way that the Xenta 121 runs cooling outside of cooling mode.
  1. In ZBuilder > Sequences > Fan, confirm that "Run in min speed if no cooling is configured" is unchecked
  2. In ZBuilder > Sequences > Cooling, set the Cooling from "Not used" to "On/off"
  3. Change the Activate at from 0% to 100% TL
  4. Go back and set the Cooling to "Not used"
  5. Apply/Save changes and the fan should not cycle on in cool mode
Tags (2)
  • 3037
  • minimum