Xenta 121-FC SNVTs show up in LonMaker or NL220 but are missing in Vista
  • Xenta 121-FC SNVTs show up in LonMaker or NL220 but are missing in Vista
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 02:23 PM
  • Xenta 121-FC
  • LonMaker/NL220
  • Vista Workstation 4.5
  • System Plug-in
A problem has occurred with the import of the controller into the Vista database.
  1. In the Vista System Plug in, delete the controller from the TAC Network.
  2. In the LNS network tab, right click on the controller and disable it from being updated in the TAC Network.
  3. Update the TAC Vista Database
  4. Refresh the Folder View in Vista Workstation.
  5. Verify that the controller has been removed from Vista.
  6. In the Vista System Plug in, re-enable the controller to be updated in the TAC Network
  7. Move it back into its former location in the TAC Network
  8. Update the Vista Database a second time.
  9. Go to Vista Workstation, verify that the controller has returned and values are being properly displayed.