Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Xenta 104-A firmware version compatibility

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta 104-A firmware version compatibility
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1764 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta 104-A firmware version compatibility

Picard Product_Support
‎2018-09-10 10:13 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:29 AM

Issue

If there are already TAC Xenta 104-A devices commissioned in an LNS database, then it may not be possible to add TAC Xenta 104-A controllers of different system versions into the same database. Nor is it possible to do a replace. Certain firmware versions of the 104-A controller are not compatible with one another. Trying to add a different system version to an existing database will produce an interface does not match error. For more information on this error, see The new program interface does not match the previously defined program interface. (Subsystem: NS, #....

Product Line

TAC Vista

Environment

  • NL220
  • LonMaker
  • Vista

Cause

The incompatibility between different system versions of the TAC Xenta 104-A controller is due to a change that was made in the size of the SNVT declaration area residing in the device memory. The change in device memory occurred between version 1.10 and 1.20. For the same Program ID, LNS requires this size to be the same as previously commissioned devices.

Resolution

  1. The first action that should be taken is to update the LNS network to the most recent version. It has been confirmed that newer LNS versions have addressed this issue so that no further action is required. With newer LNS software, different version types of the TAC Xenta 104-A may be added to the same database. 
  2. If upgrading the LNS software is not an option, the firmware in the controllers can be upgraded as a work around to correct the issue. In order for a TAC Xenta 104-A controller with version 1.10 to reside in the same database as version 1.20, the 1.20 controller must be upgraded to version 1.20A. In similar fashion, version 1.21 must be upgraded to version 1.21A to coincide with version 1.10. To add a 104-A controller with version 1.21 to a database with version 1.20 already on it, no further action need be taken. Version 1.20 and 1.21 are compatible.
    It is important to reference the compatibility matrix found below. Changing the firmware to an "A" version will then make the controller incompatible with versions 1.20 and 1.21. Also note that it is not possible to upgrade from system version 1.10 to 1.20/1.21 due to the memory configuration.The modified "A" versions will not be loaded into the controllers from the factory. These NXE/APB files will only be available on the Buildings Business Extranet. To download the NXE/APB file for v1.20A or v1.21A, go to The Exchange Download Center. Perform a search for TAC Xenta 104-A Firmware. The 1.20A version will be labeled "TAC Xenta 104-A Version 1.20 (78 Kb)" and the 1.21A version will be labeled "TAC Xenta 104-A Version 1.21A (45 Kb)".
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 8136
  • old
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore