Issue
- When the Xenta 104-A goes from occupied to unoccupied mode, it switches from HVAC_COOL to HVAC_HEAT.
- This shows up on the graphic by the nvoEffectiveStpt showing the UNOCCUPIED_HEAT setpoint when the UNOCCUPIED_COOL was expected.
Environment
Xenta 104-A
Cause
Switching from occupancy mode, or override mode, causes the 104-A to go into HVAC_HEAT mode unexpectedly.
Resolution
-
The above graphic shows the room temperature over time as a red/blue line.
- When the line is shown in red, the 104-A would be in HVAC_HEAT mode.
- When the line is shown in blue, the 104-A would be in HVAC_COOL mode.
- Make note that on the first program cycle, if the box is occupied, but the temperature is below the OCCUPIED_COOL setpoint, it will default to HVAC_HEAT mode.
-
During the occupied time, the box performs as expected.
- If the temperature rises above the OCCUPIED_COOL setpoint, the box goes into HVAC_COOL mode.
- If the temperature falls below the OCCUPIED_HEAT setpoint, the box goes into HVAC_HEAT mode.
- Make note of the circled portion of the chart. When the RTU transitions from occupied to unoccupied mode, if the temperature is below the UNOCCUPIED_COOL setpoint, it will default to HVAC_HEAT mode, even if it was in HVAC_COOL prior to the transition. The unit will not be calling for heat, but will display the heating setpoint on the effective setpoint output.