Xenta 102-AX space temperature calibration through Vista Workstation
  • Xenta 102-AX space temperature calibration through Vista Workstation
‎2018-09-06 01:36 PM
Xenta 102-AX space temperature sensor calibration offset can be set through Vista Workstation. If using degrees Fahrenheit, it is helpful to change the units on that value from "°F" to "°F, diff" to eliminate the 32° offset and make it more intuitive to the user.
  • Xenta 102-AX
  • Vista Workstation
  • Classic Network
  • UCPTvavSelection.CSS
0°C (whether a temperature value or an offset value) converts to 32°F. If referring to an offset value, the units of °F, diff eliminate this 32° offset.
  1. Navigate to the VAV in the network structure in Workstation
  2. Go to VAV_Controller and find UCPTvavSelection.CSS
  3. Double click the value
  4. Click on the Unit field and choose °F, diff from the drop down menu
  5. Click OK
  6. Open the value again, now enter any desired calibration offset for the space temperature.
Tags (2)
  • 5677
  • adjust