Issue
Xenta 102-AX effective setpoint output is perpetually offset by a fixed unadjustable amount
Environment
Xenta 102-AX
Cause
There is a variable in the memory of the Xenta 102-AX that can offset the space temperature setpoint. It is set when adjusting the space temperature setpoint with an M/STAT and pressing Enter -- which is not a step required to make the adjustment. From then on, this other variable will feed the M/STAT/STR-250 adjustment.
Resolution
The only way to clear the invisible offset is the same way it was set: Configure the setpoint displa...