Xenta 102-AX Plug-In and AirFlow Reset (%) default value
  • Xenta 102-AX Plug-In and AirFlow Reset (%) default value
  • SESA116857
    SESA116857
‎2018-09-06 01:25 PM
When writing the invalid value (163.835) to the Airflow Reset (%) in the Xenta 102-AX plug-in, the value is only changed to 163.830 and the airflow setpoint is set to the Maximum airflow setpoint.
The Xenta 102-AX plug-in does not support 3 decimal places of precision and will only write a 163.830 value to the device. The plug-in will state this is an invalid value because it is over 100, but it will treat the airflow reset like it is configured as 100%.
  • Power cycle the Xenta 102-AX controller to revert the nviAirFlowReset SNVT to the invalid value (163.835)
  • Use the LNS Browser to manually write the value 163.835 to the nviAirFlowReset SNVT on the VAV Controller function block.
  • 5950