Xenta 102-AX Damper and Floating Output Resynchronization
  • Xenta 102-AX Damper and Floating Output Resynchronization
  • Anonymous user
‎2018-09-06 02:18 PM
How and when does a Xenta 102-AX resynchronize its damper floating output control?
Xenta 102-AX v2.17 and up
Documented reasons for a damper and floating output resynchronization on a Xenta 102-AX controller
There are 5 events that cause a Xenta 102-AX to resynchronize its floating control logic for the damper and other outputs. These reasons are:
  1. At controller reset. (This could be a power cycle or reset command via TAC Vista/LNS)
  2. If the damper motor position command has been inside its "active zone" (5% - 95%) for an accumulated time of 24 hours, AND the motor position then goes to 0% or 100% (Note that the outputs and damper are timed and reset independent of each other)
  3. Indication of error in flow detection. This is if nvoFlowControlPt = 0 but nvoMotorPositn > 0 for 1 minute or more
  4. If nviEmergCmd is set to any of the following modes:
    • EMERG_PRESSURIZE
    • EMERG_DEPRESSURIZE
    • EMERG_PURGE
    • EMERG_SHUTDOWN
    and then goes back to EMERG_NORMAL
  5. A controller reset via Lonmaker or NL220 will also cause a resynchronization of the damper and the other floating outputs. This is necessary if the stroke time (throttling range) or stroke direction is changed in the middle of a damper operation
  • 4280